[SOLVED] NUT Client configuration -> help needed for shutdown Proxmox host

Ronny1978

Member
Mar 13, 2023
62
14
8
Hello Together.

I hope you can help me?

I meet the following requirements:

- Synology DS918+ as NUT Server
- Proxmox host as NUT Client
- APC 1000 with USB connection to Synology DS918+

What works?

- the connection between DS918+ and Proxmox host is established and works
- sending emails from Proxmox host, when NUT connection is lost, established, on batt or online again

What doesn't works?

I want to shut down Proxmox host with "upsmon -c fsd" after 180 seconds after change to ONBATT, but the script doesn't starts. If I execute "upsmon -c fsd" in the Proxmox shell for testing, it works fine. So I think I have a problem with the upssched-cmd. Here me configurations:

nut.conf
Code:
MODE=netclient

upsmon.conf
Code:
RUN_AS_USER root
MONITOR ups@192.168.1.20 1 monuser Secret slave
NOTIFYCMD /etc/nut/notify

MINSUPPLIES 1
SHUTDOWNCMD "/sbin/shutdown -h +0"
POLLFREQ 5
POLLFREQALERT 5
HOSTSYNC 15
DEADTIME 15
POWERDOWNFLAG /etc/killpower

NOTIFYMSG ONLINE        "UPS %s ist wieder Online"
NOTIFYMSG ONBATT        "UPS %s ist im Akkumodus"
NOTIFYMSG LOWBATT       "UPS %s Batterie ist niedrig"
NOTIFYMSG FSD           "UPS %s: forced shutdown in progress"
NOTIFYMSG COMMOK        "Kommunikation mit UPS %s ist wieder hergestellt"
NOTIFYMSG COMMBAD       "Kommunikation mit UPS %s unterbrochen"
NOTIFYMSG SHUTDOWN      "Auto logout and shutdown proceeding"
NOTIFYMSG REPLBATT      "UPS %s Batterie muss ersetzt werden"
NOTIFYMSG NOCOMM        "UPS %s ist nicht erreichbar"
NOTIFYMSG NOPARENT      "upsmon Prozess  - shutdown ist unmöglich"

ONLINE   : UPS is back online
ONBATT   : UPS is on battery
LOWBATT  : UPS has a low battery (if also on battery, it's "critical")
FSD      : UPS is being shutdown by the master (FSD = "Forced Shutdown")
COMMOK   : Communications established with the UPS
COMMBAD  : Communications lost to the UPS
SHUTDOWN : The system is being shutdown
REPLBATT : The UPS battery is bad and needs to be replaced
NOCOMM   : A UPS is unavailable (can't be contacted for monitoring)
NOPARENT : The process that shuts down the system has died (shutdown impossible)


NOTIFYFLAG ONLINE       SYSLOG+WALL+EXEC
NOTIFYFLAG ONBATT       SYSLOG+WALL+EXEC
NOTIFYFLAG LOWBATT      SYSLOG+WALL+EXEC
NOTIFYFLAG FSD          SYSLOG+WALL+EXEC
NOTIFYFLAG COMMOK       SYSLOG+WALL+EXEC
NOTIFYFLAG COMMBAD      SYSLOG+WALL+EXEC
NOTIFYFLAG SHUTDOWN     SYSLOG+WALL+EXEC
NOTIFYFLAG REPLBATT     SYSLOG+WALL
NOTIFYFLAG NOCOMM       SYSLOG+WALL
NOTIFYFLAG NOPARENT     SYSLOG+WALL

RBWARNTIME 43200

NOCOMMWARNTIME 180

FINALDELAY 5

upssched.conf
Code:
CMDSCRIPT /etc/nut/upssched-cmd
PIPEFN /etc/nut/upssched.pipe
LOCKFN /etc/nut/upssched.lock

AT ONBATT * START-TIMER onbatt 180
AT ONBATT * EXECUTE onbatt
AT ONLINE * CANCEL-TIMER onbatt online
AT LOWBATT * EXECUTE onbatt
AT COMMBAD * START-TIMER commbad 120
AT COMMOK * CANCEL-TIMER commbad commok
AT NOCOMM * EXECUTE commbad
AT SHUTDOWN * EXECUTE powerdown

upssched-cmd
Code:
#!/bin/sh
case $1 in
onbatt)
logger -t upssched-cmd "UPS running on battery"
/usr/sbin/upsmon -c fsd
;;
earlyshutdown)
logger -t upssched-cmd "UPS on battery too long, early shutdown"
/usr/sbin/upsmon -c fsd
;;
shutdowncritical)
logger -t upssched-cmd "UPS on battery critical, forced shutdown"
/usr/sbin/upsmon -c fsd
;;
upsgone)
logger -t upssched-cmd "UPS has been gone too long, can't reach"
;;
*)
logger -t upssched-cmd "Unrecognized command: $1"
;;
esac

For your help many thanks in advance. Have a nice weekend and please stay healthy.

Ronny
Chemnitz / Germany
 
Hi / Guten tag.
So did you figure out how to run the script for shutdown ? And was it one to close all vm first and the shutdown prox after ?
 
So did you figure out how to run the script for shutdown ? And was it one to close all vm first and the shutdown prox after ?
Yes. The script shutdown all VM's and LXC containers first, then Proxmox shutdown itself. My Synology DS918+ send a wake on LAN command, when the power is replaced. Proxmox send me an email for each step -> (1. Warning shutdown / 2. Shutdown / 3. Lost communication battery / 4. Communication battery rebuild).

It works fine.

Have a nice weekend.

Ronny
 
@Ronny1978 Did you do any further modification to your script? I get the notification that my ups is on battery in sysylog but my proxmox does not shutdown.

Thanks
 
UPSMON.conf
Code:
RUN_AS_USER root
MONITOR ups@ip address NAS 1 monuser secret slave

MINSUPPLIES 1
SHUTDOWNCMD "/sbin/shutdown -h"
NOTIFYCMD /usr/sbin/upssched
POLLFREQ 2
POLLFREQALERT 1
HOSTSYNC 15
DEADTIME 15
POWERDOWNFLAG /etc/killpower

NOTIFYMSG ONLINE    "UPS %s ist wieder online"
NOTIFYMSG ONBATT    "UPS %s ist im Akkumodus"
NOTIFYMSG LOWBATT   "UPS %s Batterie ist niedrig"
NOTIFYMSG FSD       "UPS %s: forced shutdown in progress"
NOTIFYMSG COMMOK    "Kommunikation mit UPS %s wieder hergestellt"
NOTIFYMSG COMMBAD   "Kommunikation mit UPS %s verloren"
NOTIFYMSG SHUTDOWN  "Auto logout and shutdown proceeding"
NOTIFYMSG REPLBATT  "UPS %s battery needs to be replaced"
NOTIFYMSG NOCOMM    "UPS %s ist nicht erreichbar"
NOTIFYMSG NOPARENT  "upsmon parent process died - shutdown impossible"

NOTIFYFLAG ONLINE   SYSLOG+WALL+EXEC
NOTIFYFLAG ONBATT   SYSLOG+WALL+EXEC
NOTIFYFLAG LOWBATT  SYSLOG+WALL
NOTIFYFLAG FSD      SYSLOG+WALL+EXEC
NOTIFYFLAG COMMOK   SYSLOG+WALL+EXEC
NOTIFYFLAG COMMBAD  SYSLOG+WALL+EXEC
NOTIFYFLAG SHUTDOWN SYSLOG+WALL+EXEC
NOTIFYFLAG REPLBATT SYSLOG+WALL
NOTIFYFLAG NOCOMM   SYSLOG+WALL+EXEC
NOTIFYFLAG NOPARENT SYSLOG+WALL

UPSSCHED.conf

Code:
GNU nano 5.4                                                             upssched.conf                                                                     
CMDSCRIPT /etc/nut/upssched-cmd
PIPEFN /etc/nut/upssched.pipe
LOCKFN /etc/nut/upssched.lock

AT ONBATT * START-TIMER onbatt 600
AT ONLINE * CANCEL-TIMER onbatt online
AT LOWBATT * EXECUTE onbatt
AT COMMBAD * EXECUTE commbad_message
AT COMMOK * EXECUTE commok_message
AT NOCOMM * EXECUTE nocomm_message
AT SHUTDOWN * EXECUTE shutdown_message
AT SHUTDOWN * EXECUTE powerdown

UPSSCHED CMD
Code:
  GNU nano 5.4                                                             upssched-cmd                                                                       
#!/bin/sh

 case $1 in
       onbatt)
          logger -t upssched-cmd "UPS im Akkumodus"
          /usr/sbin/upsmon -c fsd
          ;;
        commbad_message)
          echo "UPS ist nicht mehr verbunden" | mailx -s "Proxmox: UPS Warnmeldung" e-mail address for warning
          ;;
        online)
          logger -t upssched-cmd "UPS wieder Online"
          ;;
        commok_message)
          echo "UPS ist wieder verbunden" | mailx -s "Proxmox: UPS Warnmeldung" e-mail address for warning
          ;;
        nocomm_message)
          echo "UPS ist nicht mehr erreichbar" | mailx -s "Proxmox: UPS Warnmeldung" e-mail address for warning
          ;;
        shutdowncritical)
          logger -t upssched-cmd "UPS on battery critical, forced shutdown"
          ;;
        upsgone)
          logger -t upssched-cmd "UPS has been gone too long, can't reach"
          ;;
        shutdown_message)
          echo "Proxmox wird heruntergefahren" | mailx -s "Promox: UPS Warnmeldung" e-mail address for warning
          ;;
       *)
          logger -t upssched-cmd "Unrecognized command: $1"
          ;;
 esac

Thats work for me.
 
I've modified upssched-cmd so that it automatically uses the root email address and puts the hostname of the Proxmox host in the subject.

Code:
#!/bin/sh

EMAIL=`cat /etc/pve/user.cfg | grep root | awk '{split($0,a,":"); print a[7]}'`
PROXMOXHOST=$(uname -n)

 case $1 in
       onbatt)
          logger -t upssched-cmd "UPS on battery"
          /usr/sbin/upsmon -c fsd
          ;;
        commbad_message)
          echo "UPS is not connected" | mailx -s "Proxmox ($PROXMOXHOST): UPS Warning" $EMAIL
          ;;
        online)
          logger -t upssched-cmd "UPS Online"
          ;;
        commok_message)
          echo "UPS is connected again" | mailx -s "Proxmox ($PROXMOXHOST): UPS Warning" $EMAIL
          ;;
        nocomm_message)
          echo "UPS is not reachable" | mailx -s "Proxmox ($PROXMOXHOST): UPS Warning" $EMAIL
          ;;
        shutdowncritical)
          logger -t upssched-cmd "UPS on battery critical, forced shutdown"
          ;;
        upsgone)
          logger -t upssched-cmd "UPS has been gone too long, can't reach"
          ;;
        shutdown_message)
          echo "Proxmox shutdown" | mailx -s "Promox ($PROXMOXHOST): UPS Warning" $EMAIL
          ;;
       *)
          logger -t upssched-cmd "Unrecognized command: $1"
          ;;
 esac
 
Thanks for the configuration examples as well as the upssched-cmd examples - that's very helpful (and kinda unexpected that the defaults aren't more... sane/helpful).

Anyways, i kinda got the same setup around here - Synology is the master, connected via USB cable to a Cyberpower UPS.

Question is, if anyone has recommendations how to handle the shutdown order in a 3-server setup with Ceph?

I mean, i can power down one of three without much of a problem - but after that - is there a preferred sequence? Timeouts to configure? Something? :)

Thanks!
 
Yes. The script shutdown all VM's and LXC containers first, then Proxmox shutdown itself. My Synology DS918+ send a wake on LAN command, when the power is replaced. Proxmox send me an email for each step -> (1. Warning shutdown / 2. Shutdown / 3. Lost communication battery / 4. Communication battery rebuild).

It works fine.

Have a nice weekend.

Ronny
Hello. And how this is implemented can be found in more detail: My Synology DS918+ send a wake on LAN command, when the power is replaced
 
Hello @sany_ch ,

I don't know, if I understand you correctly. When the DS918+ has replaced power and starts, after startup it sends via script the following command to proxmox:

Code:
/usr/syno/sbin/synonet --wake 00:e0:4c:88:0d:80 ovs_bond0
 
  • Like
Reactions: sany_ch
When the DS918+ has replaced power and starts
Not sure of use-case scenario, but surely the Synology device has also been (safely) powered down due to a power failure, what brings the Synology device backup automatically, when power has been restored? More likely you want a box-system/OS that isn't affected by sudden loss of power & can be set to always be/turn-back on when power is online. Don't think Synology device cuts the deal.
 
Last edited:
Don't think Synology device cuts the deal.
It does ;-). The Synology gets the information from the USV via USB. Then its send a signal to my Proxmox to shutdown. If the power is replaced, the Synology starts up and starts a script -> WoL to Proxmox Host. Promox started also. It works very well.
 
  • Like
Reactions: gfngfn256