I'm setting up NUT on my primary Proxmox node and I'm running into an issue. When the 'upsmon -c fsd' command is executed, it takes 3 minutes for the system to actually shutdown. Even if I don't have any VM or LXC running, it takes 3 minutes to start the shutdown. So there is some timer that is waiting to expire I assume.
On my other Proxmox node, it executes the shutdown immediately, even if I have VM's running.
The syslog doesn't appear to show anything.. As far as I can tell, the config files are the same for the NUT config files.
Anyone have ideas? My Google fu hasn't been able to find an answer for this.
Edit: Found the setting!! There is a setting in the upsmon.conf called 'FINALDELAY' that was set to 180 seconds instead of 5 like the other host.
On my other Proxmox node, it executes the shutdown immediately, even if I have VM's running.
The syslog doesn't appear to show anything.. As far as I can tell, the config files are the same for the NUT config files.
Anyone have ideas? My Google fu hasn't been able to find an answer for this.
Edit: Found the setting!! There is a setting in the upsmon.conf called 'FINALDELAY' that was set to 180 seconds instead of 5 like the other host.